posted 05-20-2014 10:58 AM ET (US)
Dave--I suspect that the devices you call "switches" and assign a current rating of 10-Amperes are probably actually circuit breakers. They are the over current protection for branch circuits that distribute power from the primary power distribution to the helm area. To know if you can use one of the 10-Ampere branch circuits of the "ACCS" group to provide power to the Lenco Trim Tab actuators, you have to find out how much electrical power is needed by that load.
Check with the manufacturer to see what the power requirements are for the load. If the load is 10-Amperes or less, you can use one of the existing branch circuits with the 10-Ampere circuit breaker. If you need a circuit with more capacity, you must make a modification to the electrical panel.
One option may be to replace one of the existing 10-Ampere circuit breakers with a new circuit breaker of the same style and type but with a higher current rating. Here I am assuming that one of the existing 10-Ampere circuit breakers is presently not feeding any loads and is unused.
If you do not have any unused branch circuits, you will have to install a new branch circuit. To install a new branch circuit you will need a new circuit breaker, and some place to install it. Often there are blank and unoccupied cut-outs on the circuit breaker panel that are ready to be used for installation of a new branch circuit.
When connecting an electrical load to the branch circuit power distribution at the circuit breaker panel, you must use proper wiring practices, and select the conductor size to be appropriate for the length of the circuit and the current that will be flowing. This is necessary to keep the voltage drop on the circuit to be acceptable.
Let's start with the first step: how much electrical current is needed by your new load?